Welcome to the Australian Ford Forums forum. You are currently viewing our boards as a guest which gives you limited access to view most discussions and inserts advertising. By joining our free community you will have access to post topics, communicate privately with other members, respond to polls, upload content and access many other special features without post based advertising banners. Registration is simple and absolutely free so please, join our community today! If you have any problems with the registration process or your account login, please contact us. Please Note: All new registrations go through a manual approval queue to keep spammers out. This is checked twice each day so there will be a delay before your registration is activated. |
|
The Pub For General Automotive Related Talk |
|
Thread Tools | Display Modes |
19-01-2024, 04:47 PM | #1 | ||
FG XR6 Ute & Sedan
Join Date: Oct 2006
Location: Bibra Lake WA
Posts: 23,524
|
Like most people you probably all know you should not try to plug a 15amp device into a 10amp outlet or modify the cord or worse the plug so you could. But you also probably assumed like many, including me until today, that it was OK to plug a 10amp plug or device into a 15amp socket as they normally fit and appear to work fine. But I learnt today this is actually not the case.
I have a double 15amp outlet in my shed I had installed some years ago (when I bought my car lift) by an electrician with both separately fused so I could use both the car lift and a mig welder in my shed. I recently bought a Jamec Penn Wal Mounted tyre inflater to use with my Woodstar CP16 wall mounted compressor and decided that the most convenient place to hang this in terms of using it to fill tyres and to avoid having to use long extension cords or long hose lines was alongside the 15amp twin outlet and utilise that outlet with these two 10amp devices. However, when I came to plug them in I found that these 15 amp outlets were safety shuttered so that unless a 15 amp earth was in the earth pin socket access to active and neutral were blocked. Enquires to the Bunnings Workshop site about if suitable adapters existed initially resulted in advice that “I've spoken with HPM, and their HPM 15A Double Powerpoint will accept a 10A plug. Alternatively, it might be worth installing a 10A outlet next to your 15A” but subsequently the revised advice: “However, speaking with Deta, they have strongly advised that you do not force a 10A plug into their 15A socket as the shutters have been introduced to exclude 10A plugs; the reason is as follows: A circuit designed for 15A devices has suitable overload protection designed for them. It's best to run 10A devices on a circuit designed for them so the overload protection trips immediately if something goes wrong. A failing 10A device on a 15A circuit might not trip it immediately. If, for some reason, the overload is not triggered and the 10A cable or device overheats, it could be a fire risk.” On reflection this makes sense and so I guess it’s actually not really OK after all to plug 10amp devices into 15 amp outlets and I will be re-siting my wall mounted devices near one of the 10 amp outlets on the other side of the workshop. Adding some more 10 amp outlets would be an expensive exercise for me as my existing switchboard is full so the last electrician I used said that if I wanted to add anything more it would have to be completely replaced or an additional sub- board added and, having been through that once to replace the original asbestos backed board, I know that gets to be a very expensive exercise that I cannot justify. I don’t really want 15amp cords or plugs on the inflator and compressor as that would prevent their use with normal 10amp outlets and void the warranty. For safety reason I also don’t want to suspend cords or air hoses over the top of my car lift. What I really need is a plug in safety switch that has both RCD and overcurrent protection; something like this but with 15amp pins: https://www.bunnings.com.au/arlec-si...witch_p7050029 In any event, I though other members would like to know about this little known safety issue. Most websites when I searched, wrongly it now seems, advise it is fine to plug a 10amp device into a 15 amp outlet.
__________________
regards Blue Last edited by aussiblue; 19-01-2024 at 04:56 PM. |
||
19-01-2024, 05:01 PM | #2 | ||
Bolt Nerd
Join Date: Jan 2005
Location: Ojochal, Costa Rica (Pura Vida!)
Posts: 14,913
|
Ground down plenty of 15amp earth pins, but never thought you’d need to “add metal” to a 10amp for it to work in a 15 outlet…
__________________
Current vehicles.. Yamaha Rhino UTV, SWB 4L TJ Jeep, and boring Lhd RAV4 Bionic BF F6... UPDATE: Replaced by Shiro White 370z 7A Roadster. SOLD Workhack: FG Silhouette XR50 Turbo ute (11.63@127.44mph) SOLD 2 wheels.. 2015 103ci HD Wideglide.. SOLD SOLD THE LOT, Voted with our feet and relocated to COSTA RICA for some Pura Vida! (Ex Blood Orange #023 FPV Pursuit owner : ) |
||
19-01-2024, 05:08 PM | #3 | |||
FG XR6 Ute & Sedan
Join Date: Oct 2006
Location: Bibra Lake WA
Posts: 23,524
|
Quote:
__________________
regards Blue |
|||
5 users like this post: |
19-01-2024, 05:19 PM | #4 | ||
DIY Tragic
Join Date: Apr 2018
Location: Sydney, more than not. I hate it.
Posts: 22,547
|
So it really just requires the reverse of ye olde “15 into 10” short extension lead.
|
||
4 users like this post: |
19-01-2024, 05:51 PM | #5 | ||
64 Deluxe 4 door
Join Date: Jun 2007
Location: Raxacoricofallapatorius
Posts: 10,411
|
If your that concerned about electrical safety dont by Deta junk from Bunnos
Whats the breaker rated at? 16A is fine for a 10A outlet, just swap the outlet
__________________
XM Deluxe FG XR50 BA Pursuit Ute |
||
This user likes this post: |
19-01-2024, 06:05 PM | #6 | |||
FF.Com.Au Hardcore
Join Date: Apr 2008
Posts: 5,482
|
Quote:
__________________
HI I'M MICHAEL 2003 ACID RUSH BA FUTURA WAGON light up window switches | auto on cruise control | doubleclick window lift from remote |
|||
19-01-2024, 06:13 PM | #7 | |||
FG XR6 Ute & Sedan
Join Date: Oct 2006
Location: Bibra Lake WA
Posts: 23,524
|
Quote:
Having known several people and knowing of other people that have been fatally electrocuted i have a more than healthy respect for electricity. But I also accept a professional electrical may not always be the answer noting: a) There was an article and ongoing discussion over some months in Electronics Australia magazine about the issue some years ago noting the in those countries (or some States in some countries like USA) that either allowed home owners to do their own wiring or had schemes that gave limited licences after training to home owners the rate (not just the number) of electrocution accidents was lower in the home owner amateur electricians than in professional electricians; b) many of the recorded mortalities from electrocution involve professional electricians or their apprentices working on live wires where their co-worker or boss has tuned the power back on or they had been through the routine so many times the though they had turned power off at the main switchboard but had not (and similar "familiarity builds contempt issues"); c) when I checked the power points in my then newly built home in the early eighties with a simple three LED Clipsal tester, I found that my than half my power points were not earthed as the electrician or whoever he had install them had not stripped any insulation off the earth wire and had seemingly wrongly assumed that screwing down the earth terminal scree hard would piece the wire but this had not happened; I do wonder how many other homes built by what was then WA's largest home builder still have such faulty unearthed sockets in them; and d) the electrician that installed the 15 amp outlets in my shed had his wife call me back a few days later to see if he had reinstalled the screws holding the board onto the wall; he had not screwed the board in again but at least he had a sudden subconscious reminder though I wonder how often similar things happen that aren't remembered at all.
__________________
regards Blue Last edited by aussiblue; 19-01-2024 at 06:35 PM. |
|||
19-01-2024, 06:29 PM | #8 | |||
FG XR6 Ute & Sedan
Join Date: Oct 2006
Location: Bibra Lake WA
Posts: 23,524
|
Quote:
__________________
regards Blue |
|||
This user likes this post: |
19-01-2024, 06:38 PM | #9 | ||
Regular Member
Join Date: Jul 2007
Posts: 460
|
Never had an issue plugging a 10amp plug in a 15a GPO. I am a licensed electrician and never heard it is illegal to do so. The earth pin on a 10amp plug should be able to open the shutter on a 15a GPO.
__________________
Never argue with an idiot, they will bring you down to their level and beat with experience every time. |
||
8 users like this post: |
19-01-2024, 06:54 PM | #10 | ||
Donating Member
Join Date: Mar 2007
Location: Heading thru Hell (Corner)
Posts: 8,343
|
Yes, people don't appreciate that a circuit breaker is really there for the protection of the wiring. If the device, and therefore wiring, is designed to take 10 amps, but the circuit protection is designed to trip at a nominal 15 amp, then the 10 amp wiring is not protected at the rating it is designed for.
Naturally, there is always margin in the design so you may be able to get away with it most if the time, but it won't work all the time.
__________________
Labels are for jars, not for people. Life is a journey, not a destination. ~~~~~~~~~~~~~~ Daily: 2013 FGII EcoLPi in Winter White Play: 2015 FG X XR8 in Emperor Show' N Shine thread Gone, but not forgotten: 2015 SZII petrol Titanium Territory in Emperor |
||
This user likes this post: |
19-01-2024, 06:56 PM | #11 | ||
BLUE OVAL INC.
Join Date: Feb 2006
Posts: 8,727
|
2 pin plugs?
I see online pics show the Woodster with a 2 pin plug. |
||
19-01-2024, 07:16 PM | #12 | ||
FG XR6 Ute & Sedan
Join Date: Oct 2006
Location: Bibra Lake WA
Posts: 23,524
|
I see the Clipsal ones as with many other brands except perhaps HPM also now have this safety shutter that inhibits the insertion of a 10amp plug into their 15 amp socket so I am guessing there may been a recent change to AS/NZS 3112. the standard for AC power plugs (male) and sockets (female) requiring it.
__________________
regards Blue |
||
19-01-2024, 07:19 PM | #13 | |||
FG XR6 Ute & Sedan
Join Date: Oct 2006
Location: Bibra Lake WA
Posts: 23,524
|
Quote:
__________________
regards Blue Last edited by aussiblue; 19-01-2024 at 07:29 PM. |
|||
This user likes this post: |
19-01-2024, 08:19 PM | #14 | ||
FF.Com.Au Hardcore
Join Date: Nov 2009
Posts: 2,877
|
sounds like a 'theoretical risk' that legislation has 'fixed'
|
||
5 users like this post: |
20-01-2024, 12:49 AM | #15 | ||
HSV - I just ate one!
Join Date: Dec 2004
Location: Middle of nowhere
Posts: 3,188
|
1: your average bunnings counter jumper is hardly a reliable source.
2: DETA arent exactly a credible source either 3: safety shutters were introduced to save little johnny from sticking a fork into a GPO (power point) 4: get a licensed electrician to install a double 15a GPO that doesnt have the idiotic safety shutters, they exist.
__________________
I dont care if some prius driving eco-hippy thinks its politically incorrect for me to drive a V8..... I'm paying for the fuel! |
||
This user likes this post: |
20-01-2024, 06:39 AM | #16 | |||
Donating Member
Join Date: Mar 2007
Location: Heading thru Hell (Corner)
Posts: 8,343
|
Quote:
It's a safety issue first and foremost. That's also why it's a requirement of as3000 and has been for quite some time, IIRC.
__________________
Labels are for jars, not for people. Life is a journey, not a destination. ~~~~~~~~~~~~~~ Daily: 2013 FGII EcoLPi in Winter White Play: 2015 FG X XR8 in Emperor Show' N Shine thread Gone, but not forgotten: 2015 SZII petrol Titanium Territory in Emperor |
|||
This user likes this post: |
20-01-2024, 07:43 AM | #17 | ||
Cabover nut
Join Date: Aug 2015
Location: Onsite Eastcoast
Posts: 11,324
|
They've been selling approved 15amp to 10amp leads for the RV industry for years.
__________________
heritagestonemason.com/Fordlouisvillerestoration In order that the labour of centuries past may not be in vain during the centuries to come...... D. Diderot 1752
|
||
20-01-2024, 10:31 AM | #18 | ||
Regular Member
Join Date: Jul 2007
Posts: 460
|
The adaptors are so you can plug a 15a lead into a 10a GPO. Won't have any effect on what the subject is about.
__________________
Never argue with an idiot, they will bring you down to their level and beat with experience every time. |
||
20-01-2024, 10:54 AM | #19 | |||
FG XR6 Ute & Sedan
Join Date: Oct 2006
Location: Bibra Lake WA
Posts: 23,524
|
Quote:
2. DETA and HPM both make 15 AMP outlets so at least they would have the AS/NZS 3112 and all technical manufacturing and safety knowledge required at their fingertips. 3. But in this case also to prevent 10 amo plugs being inserted into 15 amp sockets. 4. Perhaps, but I will see where all this goes first.
__________________
regards Blue |
|||
20-01-2024, 11:23 AM | #20 | ||
Cabover nut
Join Date: Aug 2015
Location: Onsite Eastcoast
Posts: 11,324
|
and the subject is about running 10amp appliance from 15amp power point or did I miss something.
__________________
heritagestonemason.com/Fordlouisvillerestoration In order that the labour of centuries past may not be in vain during the centuries to come...... D. Diderot 1752
|
||
20-01-2024, 11:29 AM | #21 | ||
Thailand Specials
Join Date: Aug 2009
Location: Centrefold Lounge
Posts: 49,580
|
|
||
8 users like this post: |
20-01-2024, 11:35 AM | #22 | ||
Donating Member
Join Date: Mar 2007
Location: Heading thru Hell (Corner)
Posts: 8,343
|
Some of the responses in here remind me of the advice I gave years ago to another member on here: just because you can doesn't mean you should.
__________________
Labels are for jars, not for people. Life is a journey, not a destination. ~~~~~~~~~~~~~~ Daily: 2013 FGII EcoLPi in Winter White Play: 2015 FG X XR8 in Emperor Show' N Shine thread Gone, but not forgotten: 2015 SZII petrol Titanium Territory in Emperor |
||
4 users like this post: |
20-01-2024, 11:47 AM | #23 | ||
The good, bad and fugly
Join Date: Feb 2016
Posts: 1,917
|
Normally the shutters should move out of the way with a 10 Amp plug but if a bit sticky, they might need some help. With the circuit breaker off, spray the 3 holes where the plug gets inserted with silicone dry lubricant and wait for it to dry properly. Insert a 15 Amp plug several times to get the shutters moving easily again. Try the 10 Amp plug. Switch the circuit breaker back on.
Hope this works, good luck mate.
__________________
Time was on my side! |
||
20-01-2024, 11:49 AM | #24 | ||
FF.Com.Au Hardcore
Join Date: Jun 2009
Posts: 18,988
|
|
||
6 users like this post: |
20-01-2024, 01:28 PM | #25 | |||
FF.Com.Au Hardcore
Join Date: Feb 2005
Posts: 5,075
|
Quote:
|
|||
3 users like this post: |
20-01-2024, 02:30 PM | #26 | ||
The good, bad and fugly
Join Date: Feb 2016
Posts: 1,917
|
The current rating of the power point is irrelevant as they have no current limitations apart from their internal components ability to safely pass the current through to the appliances. The protection device at the switchboard dictates how much current can be delivered through the cable and power point. For this reason, 10 and 15 Amp power points can share the same circuit and protecting device. As previously mentioned by another sparky here, the fuse, circuit breaker etc are intended to protect the cable, nothing else.
__________________
Time was on my side! |
||
6 users like this post: |
20-01-2024, 03:09 PM | #27 | |||
FF.Com.Au Hardcore
Join Date: Nov 2005
Posts: 1,066
|
Quote:
The design of the 10 amp, 15 amp, 20 amp, 25 amp, and 32 amp single phase outlets is that the small can go into the bigger, but not the other way around. The physical interlock is the size and shape of the earth pin that increases with size. The 10 amp plug can go into (and open the shutters) of the 15 amp. See https://en.wikipedia.org/wiki/AS/NZS_3112 for pictures. Not sure why DETA decided to depart from a very long standing practice. Those arguing about the upstream protection size are barking up the wrong tree here as well. Most domestic power circuit are either protected by a 16 amp fuse or a 20 amp circuit breaker. (And, these days, hopefully everything is also covered by an RCD.) If one looks at the operating characteristic of both, in the overload part of the curve, they are about the same. The 20A circuit breaker is much, much, better in clearing short circuits than the 16 amp fuse. When putting a 10A plug into a 15A socket, thermal overload is not a problem as the device is limited to under 10A. The only concern is having sufficient low impedance as to clear a fault using the overcurrent part of the protective curve. Given the size of the conductor in the appliance, this is not a concern either as the cable fault rating for 1mm2 flexible is 1.2x104 A²s There are a few options ... 1) Depending on the size of the wiring and the selected circuit protection to the existing 15A outlets (e.g. 4mm cable protected by a 20A CB per 15A outlet) it is permissible under Table C9 (page 484 of AS3000) to have up to eight additional 10A socket-outlets in that circuit (under certain circumstances). 2) There are legit 15A socket-outlet to 10A plug adapters that incorporate a miniature 10A CB. This might be a cheaper option than getting a sparkie out to fix the existing 15A outlet or installing a 10A beside it. |
|||
12 users like this post: |
20-01-2024, 03:14 PM | #28 | |||
The good, bad and fugly
Join Date: Feb 2016
Posts: 1,917
|
Quote:
I understood everything that you posted and we all understand that you are a sparky (Great achievement by the way) but too much information will confuse people who aren't.
__________________
Time was on my side! |
|||
This user likes this post: |
20-01-2024, 03:43 PM | #29 | ||
FF.Com.Au Hardcore
Join Date: Apr 2008
Posts: 5,482
|
Hi. You could also put a 15 amp plug ( https://www.bunnings.com.au/hpm-15a-...g-top_p4330042 ) on to an extension cord ( https://www.bunnings.com.au/click-2m...-lead_p0189129 ) or a power board with a 10 amp circuit breaker ( https://www.bunnings.com.au/click-wh...board_p0255490 ) or a power block with breaker and RCD ( https://www.bunnings.com.au/click-4-...witch_p0135806 ). Cheers MD
__________________
HI I'M MICHAEL 2003 ACID RUSH BA FUTURA WAGON light up window switches | auto on cruise control | doubleclick window lift from remote |
||
20-01-2024, 04:07 PM | #30 | |||
FG XR6 Ute & Sedan
Join Date: Oct 2006
Location: Bibra Lake WA
Posts: 23,524
|
Quote:
__________________
regards Blue |
|||